"Several sensors were enabled with waveform recording to better understand the harmonic data composition. Figure 25 shows the waveforms from several of the sensors overlapped. The dashed line represents a perfect 60Hz sine wave with the other lines showing the readings from multiple sensors which show large distortions to the normal sine wave. A Fast Fourier Transform (FFT) of the waveforms had elevated levels of harmonic spectra, particularly below the 13th harmonic. Figure 26 shows the FFT for one of the waveforms above. Most power systems have naturally occurring odd harmonics (3rd, 5th, and 7th). However, these values were elevated during the storm. In addition, most power systems do not typically have even harmonics. The 4th, 6th, and 8th harmonics were also elevated during the storm.