Christian,
i'm skeptical that your wood floor can handle the pounds per square inch of the feet of the Nothing Rack + AS-2000 without some unpredictable deflection. whether it's deformation of the wood, or the support beneath, i'd recommend some consideration before it's all in place. if those wood slats are directly over concrete maybe you are ok. but maybe not. if it's directly over concrete i would think about cutting out the wood in that area to get directly onto the hard surface.
once it's in place and deflects (each footer will not deflect equally) it will be hard to fix it.
I already had a re-inforcement beam installed with a 30,000lb load capacity. There will be no floor bowing or deformation. It runs right underneath the equipment area/right speaker. The flooring is 1” oak on top of 1” plywood (radiant heated floor) which sits on the floor joists. Perhaps a floor plate will be in order. I can always take the top plate from my herzan AVI table unit and put the AS/AS Stand on top of that. The steel plate would disperse the feet loads more evenly.
Thanks for bringing it to my attention...